In the AirflowNetwork:SimulationControl
object, the AirflowNetwork Control input field is set to NoMultizoneOrDistribution. This effectively turns off AirFlow Network (AFN), even if you have AFN objects defined in the input file (see below).
AirflowNetwork:SimulationControl,
AirflownetworkSimulation,!- Name
NoMultizoneOrDistribution, !- AirflowNetwork Control
SurfaceAverageCalculation, !- Wind Pressure Coefficient Type
OpeningHeight, !- Height Selection for Local Wind Pressure Calculation
LowRise, !- Building Type
500, !- Maximum Number of Iterations {dimensionless}
ZeroNodePressures, !- Initialization Type
0.0001, !- Relative Airflow Convergence Tolerance {dimensionless}
0.000001, !- Absolute Airflow Convergence Tolerance {kg/s}
-.5, !- Convergence Acceleration Limit {dimensionless}
, !- Azimuth Angle of Long Axis of Building {deg}
1, !- Ratio of Building Width Along Short Axis to Width Along Long Axis
No, !- Height Dependence of External Node Temperature
SkylineLU; !- Solver
To use AFN to model window openings, you should change the AirflowNetwork Control input field to MultiZoneWithoutDistribution if you DO NOT want AFN calculations for HVAC systems (duct leakage, etc.). If you want AFN calculations for HVAC systems, then you should set this input field to either the MultiZoneWithDistribution or MultiZoneWithDistributionOnlyDuringFanOperation options instead.
Once you make this change and "turn on" AFN, I would recommend using the EMSAirflowNetworkOpeningControlByHumidity.idf example file as a reference in case there are warnings and errors related to AFN.
