Look at hours unmet per zone table in eplusout.htm file
Make sure that the zone with the problem is not a slave zone on a single-zone VAV system.
Check your thermostat setpoint schedules for this zone
Check that design days are for the same location as the weather file
Check the tolerance for reporting unmet hours
Check design/sizing temperature for each plant loop.
This is found by clicking the dashed line in the center of a plant loop.
Check the operational temperature in the plant loop's setpoint manager.
Use the BCL Measure "Add Output Variable" to request timeseries data and inspect these data in ResultsViewer to see what's going on.
Examine the zone temperatures and their thermostat setpoints
Examine the unmet hours per zone
Check sizing factor (safety factor) in model.
zone to make sure values are reasonable
---UPDATE 7/21/2015---
This Measure automates many of the checks listed below and gives you a nice report summarizing the results.