I have seen this warning, and the following info may help you understand the issue.
To fix the issue, you need to understand what you are asking the coil to do, and if it is psychometrically correct.
The relevant input settings should be found on
OS:Coil:Cooling:Water and/or OS:AirLoopHVAC.OS:Sizing:System
My approach is to leave coil settings on Autosize, which will mean that the settings in the OS:Sizing:System
will dominate.
On the OS:Sizing:System, check Central Cooling Design Supply Air Temperature and Central Cooling Design Supply Air Humidity Ratio. For bonus points, plot these on a psychometric chart vis-a-vis the air on conditions.
To see if all the above is helpful to you, try setting the Central Cooling Design Supply Air Humidity Ratio to 0.00412 ('Gee wiz, that's dry'), see if the warning changes or goes away.
To understand the hierarchy in the sizing routines, see Sizing guidance The EnergyPlus documentation in Engineering Reference, has a illuminating section on the physics of cooling coils
