Ventilation rates are specified with the DesignSpecification:OutdoorAir object in EnergyPlus.
You could write matlab script to write out the names of the DesignSpecification:OutdoorAir objects you want to change and the new ventilation rates to a .csv file, and then apply it with the OpenStudio SDK acting on an .idf file.
For example, your matlab script writes out a .csv (ventilation.csv in the example) like this:
design_oa_name,ventilation_per_area
Office WholeBuilding - Md Office Ventilation,0.000762
In this case I'm specifying ventilation per area in units of m^3/s-m^2.
You have an initial .idf file (office.idf in the example) with an existing DesignSpecification:OutdoorAir object:
DesignSpecification:OutdoorAir,
Office WholeBuilding - Md Office Ventilation, !- Name
Sum, !- Outdoor Air Method
0, !- Outdoor Air Flow per Person {m3/s-person}
0.0004318, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
0, !- Outdoor Air Flow per Zone {m3/s}
0; !- Outdoor Air Flow Air Changes per Hour {1/hr}
Use the OpenStudio SDK in a ruby script to change the DesignSpecification:OutdoorAir .idf objects:
require 'openstudio'
require 'csv'
# load the idf
idf_path = OpenStudio::Path.new("C:/path/office.idf")
workspace = OpenStudio::Workspace.load(idf_path)
workspace = workspace.get
design_oas = workspace.getObjectsByType("DesignSpecification:OutdoorAir".to_IddObjectType)
# load the ventilation data
ventilation_csv_path = "C:/path/ventilation.csv"
raw_data = CSV.table(ventilation_csv_path)
ventilation_lookup = raw_data.map { |row| row.to_hash } # transform to array of hashes
# for each DesignSpecification:OutdoorAir object, lookup the new ventilation value in the .csv file and apply it if it is defined
design_oas.each do |design_oa|
design_oa_name = design_oa.getString(0).to_s
row = ventilation_lookup.select{|r| r[:design_oa_name] == design_oa_name}
if row.empty?
puts "design oa name: #{design_oa_name} not found in lookup"
else
old_ventilation_per_area = design_oa.getDouble(3).to_f
new_ventilation_per_area = row[0][:ventilation_per_area]
design_oa.setDouble(3,new_ventilation_per_area)
puts "Changed ventilation for #{design_oa_name} from #{old_ventilation_per_area} m3/s-m2 to #{new_ventilation_per_area} m3/s-m2"
end
end
new_idf_path = "C:/path/office_new.idf"
workspace.save(new_idf_path,true)
office.idf now looks like:
0.000762, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
For more information on manipulating .idf files with the OpenStudio SDK, see the OpenStudio measure writing guide on EnergyPlus Measures. You may also find the SDK reference for IdfObjects helpful.
You could write a matlab script to write out the names of the DesignSpecification:OutdoorAir objects you want to change and the new ventilation rates to a .csv file, and then apply it with the OpenStudio SDK acting on an .idf file.
require 'csv'
# load the idf
if row.empty?
else
end
end
