Isn't that the million dollar question?
Infiltration is always a tough cookie, it's really more of an art than a science unless you can actually measure stuff (eg: blower door for enveloppe infiltration in a closed state), and even measuring can be challenging especially for larger spaces, and is usually something you do at one point in time rather than on the full range of operating conditions...
What follows below is just my quick(ish) two cents, so take it with a grain of salt.
In the case of your auditorium, you have to consider two different infiltration mechanisms:
Regular envelope infiltration: no wall, even without exterior windows or doors, is perfect, it's always permeable. You can find some default infiltration values in the ASHRAE Handbook of Fundamentals, which is generally the source for the infiltration values you'll find in the OpenStudio Library Space Types, eg for 90.1-2013 Secondary School Auditorium, that'd be 0.0446 CFM/ft², though that probably includes some windows/doors factored in. If you don't know better, you can always use this type of default value. Otherwise you can estimate and enter an equivalent Air Change per Hour (ACH) number. Note that there is also interaction between infiltration mechanisms and HVAC operation (eg: if your space is positively pressurized by your HVAC system you should expect (much) less infiltration as a result).
Doors opened before and after the event.
$$Q = 88.0 \cdot C_v \cdot A \cdot U$$
where;
(Note that the chapter has lots of other interesting info, such as infiltration from automatic doors, through an air curtain, etc, as well as examples.)