1 | initial version |
To model such a thermostat with a deadband (and anything with hysteresis as well), I see two potential ways:
Note that I haven't tested any of the two, that's going to be on you.
Zone_Temp
)Cooling_Sch_Value
)SummerDesignDay
(so that any sizing is done properly), and 80C for AllOtherDays
(maybe you want to specify the WinterDesignDay
if you have heating too...)Program:
IF Zone_Temp >= 28
Set Cooling_Sch_Value = 24
ELSEIF Zone_Temp <= 24
Set Cooling_Sch_Value = 80
ENDIF
The EMS Application Guide is a good resource, especially Example 5.
Couple of notes: you might want to pay special attention to the Capacity Control Method
of the fan coil. You might also want to to actually use something kind of a delta (Set Cooling_Sch_Value = 23.5, to ensure at some point it goes below 24C instead of modulating to meet the setpoint).
The ZoneHVAC:FourPipeFanCoil
allows for an Availability Manager List.
Perhaps you can use a combination of AVM:LowTemperatureTurnOff set to 24C and AVM:HighTemperatureTurnOn set to 28C to turn on/off the fan.
For the "Sensor" node you'll use the zone air node.