I think I got this working using EMS. Here is what I did in a Test file:
I used the expanded IDF from the Example file "HVAC Template- 5ZoneVAVWaterCooled" as a starting point.
I put in an SPM:Warmest instead of the SPM:Scheduled in the example file (with min SP 12.78C and max SP 18.33C)
I used the calling point "AfterPredictorAfterHVACManagers" for my EMS program. With this calling point, the SPM:Warmest is executed prior to the EMS program being executed.
My EMS program does these things:
a. Senses the SP values on the fan outlet node that was established by SPM:Warmest
b. Based on the current OAT value, determines a new SP for the fan outlet node as follows: For OAT >=18.33: SP=12.78C; For OAT<=12.78: SP:maintain at value established by SPM:Warmest; For OAT between 12.78 and 18.33: SP= MINIMUM of (SPM:Warmest value, Ramped limit value calculated as: (15.56-(0.5*(OAT-12.78))))
c. Establishes new SP values for the mixed air outlet based on the new Fan Outlet SP, and for the cooling coil outlet
(as would normally be done by the SPM:MixedAir, and as demonstrated in Example 1 of the EMS Application
Guide.
In my question, I had mentioned that I was concerned that the SPM:Warmest was also setting flow rates to the zone, but this is not the case. E+ is handling calculation of the zone flow rates subsequent to my EMS program.
Here is a graph comparing results from the file created in Step #2 (SPM:Warmest) with my modified file using EMS to impose a variable Maximum reset limit based on OAT. Graph shows several warm OAT days in August. (I used the SFO weather file.):
The results from the file with the OAT based max reset limit show the EMS is forcing the supply SP and supply air temp down to 12.78 as desired, when OAT (ORANGE line) is above 18.33. This is resulting in lower SAT (BROWN line), lower airflows (PINK line) compared to the original SPM:Warmest results which show higher SAT(BLUE line), higher airflows (DARK GREEN line).
@Aaron Boranian, @Chandan Sharma: you both had suggested that I should use a SPM:Scheduled in order to override setpoints. My approach seems like it is working. Am I overlooking a pitfall? Please let me know if so!
Guide.
Guide.
Guide.
| 4 | No.4 Revision |
c. Establishes new SP values for the mixed air outlet outlet, and for the cooling coil outlet, based on the new Fan Outlet SP, and for the cooling coil outlet
SP,
Guide.
| 5 | No.5 Revision |
c. Establishes new SP values for the mixed air outlet, and for the cooling coil outlet, based on the new Fan Outlet SP,
Guide.Guide. This is needed to override the values that SPM:Mixed has already set at these nodes when the setpoint managers executed.
| 6 | No.6 Revision |
SP=12.78C; For OAT<=12.78: SP:maintain at value established by SPM:Warmest; SPM:Warmest; For OAT between 12.78 and 18.33:
Guide. This is needed to override the values that SPM:Mixed SPM:Mixed has already set at these nodes when the setpoint managers executed.
In my question, I had mentioned that I was concerned that the SPM:Warmest SPM:Warmest was also setting flow rates to the zone, but this is not the case. E+ is handling calculation of the zone flow rates subsequent to my EMS program.
Here is a graph comparing results from the file created in Step #2 (SPM:Warmest) (SPM:Warmest) with my modified file using EMS to impose a variable Maximum reset limit based on OAT. Graph shows several warm OAT days in August. (I used the SFO weather file.):
@Aaron Boranian, @Chandan Sharma: you both had suggested that I should use a SPM:Scheduled SPM:Scheduled in order to override setpoints. My approach seems like it is working. Am I overlooking a pitfall? Please let me know if so!
| 7 | No.7 Revision |
Guide. This is needed to override the values that has already set at these nodes when the setpoint managers executed. SPM:MixedSPM:MixedAir
| 8 | No.8 Revision |
Guide. This is needed to override the values that SPM:MixedAir has already set at these nodes when the setpoint managers executed.
Here is the EMS:
EMS-based Setpoint Managers, !- Name
AfterPredictorAfterHVACManagers, !- EnergyPlus Model Calling Point
VAV_1_Setpoint; !- Program Name 1
OAT, !- Name
*, !- Output:Variable or Output:Meter Index Key Name
Site Outdoor Air Drybulb Temperature; !- [C] Output:Variable or Output:Meter Name
Warmest, !- Name
VAV Sys 1 Supply Fan Outlet,!- Output:Variable or Output:Meter Index Key Name
System Node Setpoint Temperature; !- [C] Output:Variable or Output:Meter Name
T_VAV1FanIn, !- Name
VAV Sys 1 Heating Coil Outlet, !- Output:Variable or Output:Meter Index Key Name
System Node Temperature; !- Output:Variable or Output:Meter Name
T_VAV1FanOut, !- Name
VAV Sys 1 Supply Fan Outlet, !- Output:Variable or Output:Meter Index Key Name
EnergyManagementSystem:Actuator,
VAV_1_SAT_setpoint, !- Name
VAV Sys 1 Supply Fan Outlet, !- Actuated Component Unique Name
System Node Setpoint, !- Actuated Component Type
Temperature Setpoint; !- Actuated Component Control Type
VAV_1_MixedAir_Setpoint, !- Name
VAV Sys 1 Mixed Air Outlet,!- Actuated Component Unique Name
VAV_1_CCOutlet_Setpoint, !- Name
VAV Sys 1 Cooling Coil Outlet,!- Actuated Component Unique Name
VAV_1_Setpoint, !- Name
IF OAT>=18.33,
SET FanOutletSetpoint = 12.78,
ENDIF,
IF OAT<=12.78,
SET FanOutletSetpoint = Warmest,
ENDIF,
IF OAT>12.78 && OAT<18.33,
SET WSPM = Warmest,
SET OA = OAT,
SET FanOutletSetpoint = @MIN (15.56-(0.5*(OAT-12.78))) Warmest,
ENDIF,
SET VAV_1_SAT_setpoint = FanOutletSetpoint, !- Program Line 1
SET VAV_1_CCOutlet_Setpoint = FanOutletSetpoint - ( T_VAV1FanOut - T_VAV1FanIn), !- Program Line 1
SET VAV_1_MixedAir_Setpoint = FanOutletSetpoint - ( T_VAV1FanOut - T_VAV1FanIn); !- <none>