In eQuest, outdoor air and exhaust air requirements specified at the zone level take precedence over values specified at the system level. So, although you tried to make your system 100% OSA with the system input for MIN-OUTSIDE-AIR, this is being ignored due to your input of an exhaust flow at the zone level. From the help (right click on field) for MIN-OUTSIDE-AIR:
If you enter MIN-OUTSIDE-AIR as well as the ZONE keywords OUTSIDE-AIR-FLOW, OA-CHANGES, OA-FLOW/PER or EXHAUST-FLOW, the ZONE values take precedence.
So, to correct: you should specify that there is 100% outside air flow at the zone level probably by specifing OUTSIDE-AIR-FLOW in cfm for each zone.