Don't you have a mechanical engineer on the project responsible to size the data center cooling system?
But yes, you shouldn't have any latent load, so for your coil Total kW = Sensible kW.
Without seeing your idf file (maybe you should share it), I would definitely look at how you defined your internal loads from the server. You probably used an "ElectricEquipment" object, make sure your fraction latent is set to zero there.
ElectricEquipment, , !- Name , !- Zone or ZoneList Name , !- Schedule Name , !- Design Level Calculation Method , !- Design Level {W} , !- Watts per Zone Floor Area {W/m2} , !- Watts per Person {W/person} 0, !- Fraction Latent 1, !- Fraction Radiant 0, !- Fraction Lost ; !- End-Use Subcategory
ElectricEquipment,
, !- Name
, !- Schedule Name
0, !- Fraction Lost
ElectricEquipment,