Autosizing requires input for operating conditions. Sizing:Zone objects are required and Sizing:System objects will be required to size air loop equipment. The best way to tell which example files have a specific object is to look at the ExampleFiles-ObjectsLink.html file.
To autosize your model, turn on the appropriate Do * Sizing Calculation input by entering Yes. Each of these fields will also require a Sizing:Zone, Sizing:System, or Sizing:Plant object, respectively. Look at the InputOutputReference document for a description of these objects.
SimulationControl,
Yes, !- Do Zone Sizing Calculation
Yes, !- Do System Sizing Calculation
Yes, !- Do Plant Sizing Calculation
Yes, !- Run Simulation for Sizing Periods
Yes; !- Run Simulation for Weather File Run Periods
Then add the appropriate sizing object. For example, for zone sizing, use a Sizing:Zone object:
Sizing:Zone,
SPACE1-1, !- Zone or ZoneList Name
SupplyAirTemperature, !- Zone Cooling Design Supply Air Temperature Input Method
14., !- Zone Cooling Design Supply Air Temperature {C}
, !- Zone Cooling Design Supply Air Temperature Difference {deltaC}
SupplyAirTemperature, !- Zone Heating Design Supply Air Temperature Input Method
50., !- Zone Heating Design Supply Air Temperature {C}
, !- Zone Heating Design Supply Air Temperature Difference {deltaC}
0.009, !- Zone Cooling Design Supply Air Humidity Ratio {kgWater/kgDryAir}
0.004, !- Zone Heating Design Supply Air Humidity Ratio {kgWater/kgDryAir}
SZ DSOA SPACE1-1, !- Design Specification Outdoor Air Object Name
0.0, !- Zone Heating Sizing Factor
0.0, !- Zone Cooling Sizing Factor
DesignDayWithLimit, !- Cooling Design Air Flow Method
, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
, !- Cooling Minimum Air Flow Fraction
DesignDay, !- Heating Design Air Flow Method
, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
; !- Heating Maximum Air Flow Fraction
The DesignSpecification:OutdoorAir object is used to specify how much outdoor air and by what method you will supply to each zone. You can also adjust the sizing factor for cooling and/or heating if needed.
DesignSpecification:OutdoorAir,
SZ DSOA SPACE1-1, !- Name
sum, !- Outdoor Air Method
0.00236, !- Outdoor Air Flow per Person {m3/s-person}
0.000305, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
0.0; !- Outdoor Air Flow per Zone {m3/s}
Sizing:Parameters,
1.0, !- Heating Sizing Factor
1.0, !- Cooling Sizing Factor
; !- Timesteps in Averaging Window
To autosize your model, turn on the appropriate Do * Sizing Calculation input by entering Yes. Each of these fields will also require a Sizing:Zone, Sizing:System, or Sizing:Plant object, respectively. If you are using ZoneHVAC equipment (baseboard, PTAC, etc.) you will need to add the Sizing:Zone object. If you are using AirloopHVAC you will need both the Sizing:Zone and Sizing:System objects. If you have a plant loop, all three sizing objects are needed. Look at the InputOutputReference document for a description of these objects.
SimulationControl,
Sizing:Zone,
Sizing:Parameters,