Find an example file that is specific to the object in question. In this example, FourPipeBeamLargeOffice.idf. Then search for the object. The notable connections in this object are the air and water node names.
Note that there are 2 air nodes, and 2 sets of water nodes. There are no coils in this object, they are inferred.
AirTerminal:SingleDuct:ConstantVolume:FourPipeBeam,
Core_bottom 4pipe Beam, !- Name
HVACOperationSchd , !- Primary Air Availability Schedule Name
HVACOperationSchd , !- Cooling Availability Schedule Name
HVACOperationSchd , !- Heating Availability Schedule Name
Core_bottom 4pipe Beam Inlet Node Name , !- Primary Air Inlet Node Name
Core_bottom 4pipe Beam Outlet Node Name , !- Primary Air Outlet Node Name
Core_bottom 4pipe Beam CW Inlet Node , !- Chilled Water Inlet Node Name
Core_bottom 4pipe Beam CW Outlet Node , !- Chilled Water Outlet Node Name
Core_bottom 4pipe Beam HW Inlet Node , !- Hot Water Inlet Node Name
Core_bottom 4pipe Beam HW Outlet Node, !- Hot Water Outlet Node Name
AUTOSIZE , !- Design Primary Air Volume Flow Rate
AUTOSIZE , !- Design Chilled Water Volume Flow Rate
AUTOSIZE , !- Design Hot Water Volume Flow Rate
AUTOSIZE , !- Zone Total Beam Length
0.036 , !- Rated Primary Air Flow Rate per Meter
597 , !- Rated Beam Cooling Capacity per Meter
10.0 , !- Rated Cooling Room Air Chilled Water Temperature Difference
5.2E-5 , !- Rated Chilled Water Volume Flow Rate per Meter
CapModFuncOfTempDiff, !- Beam Cooling Capacity Temperature Difference Modification Factor Curve or Table Name
CoolCapModFuncOfSAFlow, !- Beam Cooling Capacity Air Flow Modification Factor Curve or Table Name
CapModFuncOfWaterFlow, !- Beam Cooling Capacity Chilled Water Flow Modification Factor Curve or Table Name
1548 , !- Rated Beam Heating Capacity per Meter
27.8, !- Rated Heating Room Air Hot Water Temperature Difference
5.2E-5, !- Rated Hot Water Volume Flow Rate per Meter
CapModFuncOfTempDiff, !- Beam Heating Capacity Temperature Difference Modification Factor Curve or Table Name
HeatCapModFuncOfSAFlow, !- Beam Heating Capacity Air Flow Modification Factor Curve or Table Name
CapModFuncOfWaterFlow; !- Beam Heating Capacity Hot Water Flow Modification Factor Curve or Table Name
Now look at the induction unit example file. 5ZoneFPIU.idf.
This objects has 3 air nodes, 2 sets of water nodes, and a mixer object.
AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction,
SPACE1-1 FPIU, !- Name
ReheatCoilAvailSched, !- Availability Schedule Name
autosize, !- Maximum Total Air Flow Rate {m3/s}
1.0, !- Induction Ratio
SPACE1-1 ATU Supply Node,!- Supply Air Inlet Node Name
SPACE1-1 ATU Induc Node, !- Induced Air Inlet Node Name
SPACE1-1 In Node, !- Air Outlet Node Name
SPACE1-1 HW Coil Water In Node, !- Hot Water Inlet Node Name
SPACE1-1 CW Coil Water In Node, !- Cold Water Inlet Node Name
Coil:Heating:Water, !- Heating Coil Object Type
SPACE1-1 HW Coil, !- Heating Coil Name
autosize, !- Maximum Hot Water Flow Rate {m3/s}
0.0, !- Minimum Hot Water Flow Rate {m3/s}
0.002, !- Heating Convergence Tolerance
Coil:Cooling:Water, !- Cooling Coil Object Type
SPACE1-1 CW Coil, !- Cooling Coil Name
autosize, !- Maximum Cold Water Flow Rate {m3/s}
0.0, !- Minimum Cold Water Flow Rate {m3/s}
0.002, !- Cooling Convergence Tolerance
SPACE1-1 ATU Mixer; !- Zone Mixer Name
Here's how I would make this change.
Using a text editor:
1) find the coils and mixer specified in the induction unit object input and comment them out. Don't delete them yet since you will need the water node names.
Search for the name of the heating coil, SPACE1-1 HW Coil to find this object.
! Coil:Heating:Water,
! SPACE1-1 HW Coil, !- Name
! ReheatCoilAvailSched, !- Availability Schedule Name
! autosize, !- U-Factor Times Area Value {W/K}
! autosize, !- Maximum Water Flow Rate {m3/s}
! SPACE1-1 HW Coil Water In Node, !- Water Inlet Node Name
! SPACE1-1 HW Coil Water Out Node, !- Water Outlet Node Name
! SPACE1-1 ATU Induc Node, !- Air Inlet Node Name
! SPACE1-1 HW Coil Air Out Node, !- Air Outlet Node Name
! UFactorTimesAreaAndDesignWaterFlowRate, !- Performance Input Method
! autosize, !- Rated Capacity {W}
! 82.2, !- Rated Inlet Water Temperature {C}
! 16.6, !- Rated Inlet Air Temperature {C}
! 71.1, !- Rated Outlet Water Temperature {C}
! 32.2, !- Rated Outlet Air Temperature {C}
! ; !- Rated Ratio for Air and Water Convection
Search for the name of the cooling coil, SPACE1-1 CW Coil to find this object.
! Coil:Cooling:Water,
! SPACE1-1 CW Coil, !- Name
! CWCoilAvailSched, !- Availability Schedule Name
! autosize, !- Design Water Flow Rate {m3/s}
! autosize, !- Design Air Flow Rate {m3/s}
! autosize, !- Design Inlet Water Temperature {C}
! autosize, !- Design Inlet Air Temperature {C}
! autosize, !- Design Outlet Air Temperature {C}
! autosize, !- Design Inlet Air Humidity Ratio {kgWater/kgDryAir}
! autosize, !- Design Outlet Air Humidity Ratio {kgWater/kgDryAir}
! SPACE1-1 CW Coil Water In Node, !- Water Inlet Node Name
! SPACE1-1 CW Coil Water Out Node, !- Water Outlet Node Name
! SPACE1-1 HW Coil Air Out Node, !- Air Inlet Node Name
! SPACE1-1 CW Coil Air Out Node, !- Air Outlet Node Name
! SimpleAnalysis, !- Type of Analysis
! CrossFlow; !- Heat Exchanger Configuration
Search for the name of the zone mixer, SPACE1-1 ATU Mixer to find this object.
! AirLoopHVAC:ZoneMixer,
! SPACE1-1 ATU Mixer, !- Name
! SPACE1-1 In Node, !- Outlet Node Name
! SPACE1-1 ATU Supply Node,!- Inlet 1 Node Name
! SPACE1-1 CW Coil Air Out Node; !- Inlet 2 Node Name
2) copy the FourPipeBeam object just below the induction unit. Find the induction unit again and comment it out.
! AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction,
! SPACE1-1 FPIU, !- Name
! autosize, !- Maximum Total Air Flow Rate {m3/s}
! 1.0, !- Induction Ratio
! SPACE1-1 ATU Supply Node,!- Supply Air Inlet Node Name
! SPACE1-1 ATU Induc Node, !- Induced Air Inlet Node Name
! SPACE1-1 In Node, !- Air Outlet Node Name
! SPACE1-1 HW Coil Water In Node, !- Hot Water Inlet Node Name
! SPACE1-1 CW Coil Water In Node, !- Cold Water Inlet Node Name
! Coil:Heating:Water, !- Heating Coil Object Type
! SPACE1-1 HW Coil, !- Heating Coil Name
! autosize, !- Maximum Hot Water Flow Rate {m3/s}
! 0.0, !- Minimum Hot Water Flow Rate {m3/s}
! 0.002, !- Heating Convergence Tolerance
! Coil:Cooling:Water, !- Cooling Coil Object Type
! SPACE1-1 CW Coil, !- Cooling Coil Name
! autosize, !- Maximum Cold Water Flow Rate {m3/s}
! 0.0, !- Minimum Cold Water Flow Rate {m3/s}
! 0.002, !- Cooling Convergence Tolerance
! SPACE1-1 ATU Mixer; !- Zone Mixer Name
Now paste in the new FourPipeBeam object just below this point in the file. Copy the name of the induction unit into the new FourPipeBeam object. Copy the 2 air node names for supply air inlet and air outlet into the air nodes below. Do the same for the cooling and heating coil node names. Also copy the name of the availability schedule to the appropriate 3 inputs below, or create your own schedules. Notice we are not changing node names, that makes things much more complicated than they need to be. You can change them later if you like.
ReheatCoilAvailSched, !- Primary Air Availability Schedule Name
ReheatCoilAvailSched, !- Cooling Availability Schedule Name
ReheatCoilAvailSched, !- Heating Availability Schedule Name
SPACE1-1 ATU Supply Node, !- Primary Air Inlet Node Name
SPACE1-1 In Node, !- Primary Air Outlet Node Name
SPACE1-1 CW Coil Water In Node, !- Chilled Water Inlet Node Name
SPACE1-1 CW Coil Water Out Node, !- Chilled Water Outlet Node Name
SPACE1-1 HW Coil Water Out Node, !- Hot Water Outlet Node Name
3) Now go find the induction node name, SPACE1-1 ATU Induc Node. In this example file, it's found in a node list. Comment out the node list.
! NodeList,
! SPACE1-1 Exh Nodes, !- Name
! SPACE1-1 ATU Induc Node; !- Node 1 Name
Which connects to the zone here. Copy the exhaust node input, comment one of these, and delete the exhaust node name.
ZoneHVAC:EquipmentConnections,
SPACE1-1, !- Zone Name
SPACE1-1 Eq, !- Zone Conditioning Equipment List Name
SPACE1-1 In Nodes, !- Zone Air Inlet Node or NodeList Name
! SPACE1-1 Exh Nodes, !- Zone Air Exhaust Node or NodeList Name
SPACE1-1 Node, !- Zone Air Node Name
SPACE1-1 Out Node; !- Zone Return Air Node Name
4) Now search for the name of the induction unit, SPACE1-1 FPIU. You will find this object.
ZoneHVAC:AirDistributionUnit,
SPACE1-1 ATU, !- Name
SPACE1-1 In Node, !- Air Distribution Unit Outlet Node Name
AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction, !- Air Terminal Object Type
SPACE1-1 FPIU; !- Air Terminal Name
Change the object name AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction to AirTerminal:SingleDuct:ConstantVolume:FourPipeBeam
AirTerminal:SingleDuct:ConstantVolume:FourPipeBeam, !- Air Terminal Object Type
5) Now search for the hot water nodes and replace the heating coil type and name with the four pipe beam type and name.
Branch,
SPACE1-1 HW Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
AirTerminal:SingleDuct:ConstantVolume:FourPipeBeam, !- Component 1 Object Type
SPACE1-1 FPIU, !- Component 1 Name
SPACE1-1 HW Coil Water In Node, !- Component 1 Inlet Node Name
SPACE1-1 HW Coil Water Out Node, !- Component 1 Outlet Node Name
ACTIVE; !- Component 1 Branch Control Type
6) Do the same for the cooling coil.
Branch,
SPACE1-1 CW Branch, !- Name
SPACE1-1 CW Coil Water In Node, !- Component 1 Inlet Node Name
SPACE1-1 CW Coil Water Out Node, !- Component 1 Outlet Node Name
7) Finally, you will have to create performance curves for the following inputs. Just copy them from the example file, to your input file.
Curve:Linear, ! y = x
CapModFuncOfTempDiff, !-Name
0, !_ Coef Const
1, !- Coef x
0, !- min x
1.5, !- max x
0.0 , !- min y
1.5; ! max y
Table:OneIndependentVariable,
CoolCapModFuncOfSAFlow, !- Name
quadratic,!- Curve Type
EvaluateCurveToLimits,!- Interpolation Method
0.714,!- min x
1.2857,!- max x
0.8234,!- min y
1.1256,!- max y
dimensionless, !-
dimensionless, !-
, !- normalization ref
0.714286, 0.823403,
1.0, 1.0,
1.2857, 1.1256;
CapModFuncOfWaterFlow, !- Name
0.0,!- min x
1.333333,!- max x
0.0,!- min y
1.04,!- max y
dimensionless, !-
dimensionless, !-
0.0, 0.0,
0.05, 0.001,
0.33333, 0.71,
0.5, 0.85,
0.666667, 0.92,
0.833333, 0.97,
1.0, 1.0,
1.333333, 1.04;
HeatCapModFuncOfSAFlow, !- Name
0.714,!- min x
1.2857,!- max x
0.8554,!- min y
1.0778,!- max y
dimensionless, !-
dimensionless, !-
0.714286, 0.8554,
1.0, 1.0,
1.2857, 1.0778;
8) That's it. Check the error file to see if there are any other problems. I followed along in the induction unit example file and it runs with only report variable warnings. The converted file made with these steps C:\fakepath\5ZoneFPIU_To_FourPipeBeam.jpg is attached. Change the extension back to idf before you run it.
You should run through this exercise yourself to get familiar with this procedure. Let me know if the file does not come through as a text file.
Core_bottom 4pipe Beam, !- Now look at the induction unit example file. 5ZoneFPIU.idf.
SPACE1-1 FPIU, !- Here's how I would make this change.
! SPACE1-1 HW Coil, !- Search for the name of the cooling coil, SPACE1-1 CW Coil to find this object.
! SPACE1-1 CW Coil, !- Search for the name of the zone mixer, SPACE1-1 ATU Mixer to find this object.
! SPACE1-1 ATU Mixer, !- 2) copy the FourPipeBeam object just below the induction unit. Find the induction unit again and comment it out.
! SPACE1-1 FPIU, !- Now paste in the new FourPipeBeam object just below this point in the file. Copy the name of the induction unit into the new FourPipeBeam object. Copy the 2 air node names for supply air inlet and air outlet into the air nodes below. Do the same for the cooling and heating coil node names. Also copy the name of the availability schedule to the appropriate 3 inputs below, or create your own schedules. Notice we are not changing node names, that makes things much more complicated than they need to be. You can change them later if you like.
SPACE1-1 FPIU, !- 3) Now go find the induction node name, SPACE1-1 ATU Induc Node. In this example file, it's found in a node list. Comment out the node list.
! NodeList,
! NodeList,
! SPACE1-1 Exh Nodes, !- Which connects to the zone here. Copy the exhaust node input, comment one of these, and delete the exhaust node name.
SPACE1-1, !- Zone 4) Now search for the name of the induction unit, SPACE1-1 FPIU. You will find this object.
SPACE1-1 ATU, !- Change the object name AirTerminal:SingleDuct:ConstantVolume:FourPipeInduction to AirTerminal:SingleDuct:ConstantVolume:FourPipeBeam
SPACE1-1 ATU, !- 5) Now search for the hot water nodes and replace the heating coil type and name with the four pipe beam type and name.
Branch,
Branch,
SPACE1-1 HW Branch, !- 6) Do the same for the cooling coil.
Branch,
Branch,
SPACE1-1 CW Branch, !- 7) Finally, you will have to create performance curves for the following inputs. Just copy them from the example file, to your input file.
CapModFuncOfTempDiff, !- Beam Cooling Capacity Temperature Difference Modification Factor Curve or Table Table:OneIndependentVariable,
The converted file made with these steps C:\fakepath\5ZoneFPIU_To_FourPipeBeam.jpgis attached is attached. Change : change the extension back to idf before you run it.