HVACTemplates are used to quickly create an HVAC system for a building with one or more zones. The only inputs required are zone name, specific schedules used to control the HVAC system, and minimal other inputs to describe the desired HVAC system.
To see how HVACTemplates work, review the example files with names starting with HVACTemplate*. I do not think a template exists for ZoneHVAC:LowTemperatureRadiant:ConstantFLow.
The current template expansion program supports the following objects. These are the plant, system, thermostat, and zone templates. Typically, one of each of these is required. The plant type is used when chilled or hot water loops are needed. If there are no plant loops, this template is not used. The system type is used for each HVAC system. The thermostat type is used to populate the zones with a thermostat. And finally, the zone type is used for zone equipment in each zone.
HVACTemplate:Plant:Boiler
HVACTemplate:Plant:Boiler:ObjectReference
HVACTemplate:Plant:ChilledWaterLoop
HVACTemplate:Plant:Chiller
HVACTemplate:Plant:Chiller:ObjectReference
HVACTemplate:Plant:HotWaterLoop
HVACTemplate:Plant:MixedWaterLoop
HVACTemplate:Plant:Tower
HVACTemplate:Plant:Tower:ObjectReference
HVACTemplate:System:ConstantVolume
HVACTemplate:System:DedicatedOutdoorAir
HVACTemplate:System:DualDuct
HVACTemplate:System:PackagedVAV
HVACTemplate:System:Unitary
HVACTemplate:System:UnitaryHeatPump:AirToAir
HVACTemplate:System:UnitarySystem
HVACTemplate:System:VAV
HVACTemplate:System:VRF
HVACTemplate:Thermostat
HVACTemplate:Zone:BaseboardHeat
HVACTemplate:Zone:ConstantVolume
HVACTemplate:Zone:DualDuct
HVACTemplate:Zone:FanCoil
HVACTemplate:Zone:IdealLoadsAirSystem
HVACTemplate:Zone:PTAC
HVACTemplate:Zone:PTHP
HVACTemplate:Zone:Unitary
HVACTemplate:Zone:VAV
HVACTemplate:Zone:VAV:FanPowered
HVACTemplate:Zone:VAV:HeatAndCool
HVACTemplate:Zone:VRF
HVACTemplate:Zone:WaterToAirHeatPump
Many other objects are created when using templates. For example, the HVACTemplate_5ZoneBaseboardHeat.idf file was modified (by removing 4 of the zone baseboard heat templates) to keep only a single zone template for the baseboard. This example system uses 4 template objects.
HVACTemplate:Thermostat,
HVACTemplate:Zone:BaseboardHeat,
HVACTemplate:Plant:HotWaterLoop,
HVACTemplate:Plant:Boiler,
When this simulation is executed, the template objects will be expanded to create all required objects for the HVAC system specified. The expanded system will be saved in the expidf file and can be viewed after the simulation completes. Template objects in the input file will be commented out, and the objects added due to expansion are added at the end of the input file.
The first 4 objects below are the HVACTemplates in the original (modified) file. In the expidf file, these are commented out since they are no longer needed and have been replaced with the required EnergyPlus objects. It is apparent from this example that using templates can save a significant amount of time setting up the HVAC system.
! HVACTemplate:Thermostat,
! Heat Only, !- Name
! Htg-SetP-Sch, !- Heating Setpoint Schedule Name
! , !- Constant Heating Setpoint {C}
! No-Clg-SetP-Sch, !- Cooling Setpoint Schedule Name
! ; !- Constant Cooling Setpoint {C}
! HVACTemplate:Zone:BaseboardHeat,
! SPACE1-1, !- Zone Name
! Heat Only, !- Template Thermostat Name
! , !- Zone Heating Sizing Factor
! HotWater, !- Baseboard Heating Type
! , !- Baseboard Heating Availability Schedule Name
! autosize, !- Baseboard Heating Capacity {W}
! , !- Dedicated Outdoor Air System Name
! Flow/Person, !- Outdoor Air Method
! , !- Outdoor Air Flow Rate per Person {m3/s}
! , !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
! ; !- Outdoor Air Flow Rate per Zone {m3/s}
! HVACTemplate:Plant:HotWaterLoop,
! Hot Water Loop, !- Name
! , !- Pump Schedule Name
! INTERMITTENT, !- Pump Control Type
! Default, !- Hot Water Plant Operation Scheme Type
! , !- Hot Water Plant Equipment Operation Schemes Name
! , !- Hot Water Setpoint Schedule Name
! 82, !- Hot Water Design Setpoint {C}
! ConstantFlow, !- Hot Water Pump Configuration
! 179352, !- Hot Water Pump Rated Head {Pa}
! OutdoorAirTemperatureReset, !- Hot Water Setpoint Reset Type
! 82.2, !- Hot Water Setpoint at Outdoor Dry-Bulb Low {C}
! -6.7, !- Hot Water Reset Outdoor Dry-Bulb Low {C}
! 65.6, !- Hot Water Setpoint at Outdoor Dry-Bulb High {C}
! 10; !- Hot Water Reset Outdoor Dry-Bulb High {C}
! HVACTemplate:Plant:Boiler,
! Main Boiler, !- Name
! HotWaterBoiler, !- Boiler Type
! autosize, !- Capacity {W}
! 0.8, !- Efficiency
! NaturalGas, !- Fuel Type
! 1, !- Priority
! ; !- Sizing Factor
! New objects created from ExpandObjects
ScheduleTypeLimits,
HVACTemplate Any Number; !- Name
ThermostatSetpoint:DualSetpoint,
Heat Only Dual SP Control, !- Name
Htg-SetP-Sch, !- Heating Setpoint Temperature Schedule Name
No-Clg-SetP-Sch; !- Cooling Setpoint Temperature Schedule Name
Schedule:Compact,
HVACTemplate-Always 1, !- Name
HVACTemplate Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00, !- Field 3
1; !- Field 4
Schedule:Compact,
HVACTemplate-Always 4, !- Name
4; !- Field 4
ZoneControl:Thermostat,
SPACE1-1 Thermostat, !- Name
SPACE1-1, !- Zone or ZoneList Name
HVACTemplate-Always 4, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control Object Type
Heat Only Dual SP Control; !- Control Name
Sizing:Zone,
SupplyAirTemperature, !- Zone Cooling Design Supply Air Temperature Input Method
12.5, !- Zone Cooling Design Supply Air Temperature {C}
, !- Zone Cooling Design Supply Air Temperature Difference {delta C}
SupplyAirTemperature, !- Zone Heating Design Supply Air Temperature Input Method
50, !- Zone Heating Design Supply Air Temperature {C}
, !- Zone Heating Design Supply Air Temperature Difference {delta C}
0.008, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H20/kg-air}
0.008, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
, !- Design Specification Outdoor Air Object Name
, !- Zone Cooling Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
0, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
0, !- Cooling Minimum Air Flow Fraction {}
DesignDay, !- Heating Design Air Flow Method
0, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
0, !- Heating Maximum Air Flow Fraction {}
; !- Design Specification Zone Air Distribution Object Name
ZoneHVAC:EquipmentConnections,
SPACE1-1 Equipment, !- Zone Conditioning Equipment List Name
, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
SPACE1-1 Zone Air Node, !- Zone Air Node Name
SPACE1-1 Return Outlet; !- Zone Return Air Node Name
ZoneHVAC:EquipmentList,
SPACE1-1 Equipment, !- Name
ZoneHVAC:Baseboard:RadiantConvective:Water, !- Zone Equipment Object Type
SPACE1-1 Baseboard Heat, !- Zone Equipment Name
1, !- Zone Equipment Cooling Sequence
1; !- Zone Equipment Heating or No-Load Sequence
SPACE1-1 Baseboard Heat, !- Name
, !- Availability Schedule Name
SPACE1-1 Baseboard HW Inlet, !- Inlet Node Name
SPACE1-1 Baseboard HW Outlet, !- Outlet Node Name
87.78, !- Rated Average Water Temperature {C}
0.063, !- Rated Water Mass Flow Rate {m3/s}
HeatingDesignCapacity, !- Heating Design Capacity Method
autosize, !- Heating Design Capacity {W}
, !- Heating Design Capacity Per Floor Area {W/m2}
, !- Fraction of Autosized Heating Design Capacity
autosize, !- Maximum Water Flow Rate
0.001, !- Convergence Tolerance
0.0, !- Fraction Radiant
0.0; !- Fraction of Radiant Energy Incident on People
Branch,
SPACE1-1 Baseboard Heat HW Branch, !- Name
, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
ZoneHVAC:Baseboard:RadiantConvective:Water, !- Component Object Type
SPACE1-1 Baseboard Heat, !- Component Name
SPACE1-1 Baseboard HW Inlet, !- Component Inlet Node Name
SPACE1-1 Baseboard HW Outlet, !- Component Outlet Node Name
Active; !- Component Branch Control Type
Boiler:HotWater,
autosize, !- Nominal Capacity {W}
0.8, !- Nominal Thermal Efficiency
LeavingBoiler, !- Efficiency Curve Temperature Evaluation Variable
Main Boiler Efficiency Curve, !- Normalized Boiler Efficiency Curve Name
81, !- Design Boiler Water Outlet Temp {C}
autosize, !- Max Design Boiler Water Flow Rate {m3/s}
0.0, !- Minimum Part Load Ratio
1.1, !- Maximum Part Load Ratio
1.0, !- Optimum Part Load Ratio
Main Boiler HW Inlet, !- Water Inlet Node Name
Main Boiler HW Outlet, !- Water Outlet Node Name
100.0, !- Temp Upper Limit Water Outlet {C}
ConstantFlow, !- Boiler Flow Mode
0, !- Parasitic Electric Load {W}
1.0; !- Sizing Factor
Curve:Quadratic,
Main Boiler Efficiency Curve, !- Name
0.97, !- Coefficient1 Constant
0.0633, !- Coefficient2 x
-0.0333, !- Coefficient3 x**2
0.0, !- Minimum Value of x
1.0; !- Maximum Value of x
Branch,
Main Boiler HW Branch, !- Name
Boiler:HotWater, !- Component Object Type
Main Boiler, !- Component Name
Main Boiler HW Inlet, !- Component Inlet Node Name
Main Boiler HW Outlet, !- Component Outlet Node Name
Sizing:Plant,
Hot Water Loop Hot Water Loop, !- Plant or Condenser Loop Name
Heating, !- Loop Type
82, !- Design loop exit temperature {C}
11.0; !- Design loop delta T {deltaC}
PlantLoop,
Hot Water Loop Hot Water Loop, !- Name
Water, !- Fluid Type
, !- User Defined Fluid Type
Hot Water Loop Operation, !- PlantEquipmentOperationSchemes Name
Hot Water Loop HW Supply Outlet, !- Loop Temperature Setpoint Node Name
100, !- Maximum Loop Temperature {C}
10, !- Minimum Loop Temperature {C}
autosize, !- Maximum Loop Volumetric Flow Rate {m3/s}
0, !- Minimum Loop Volumetric Flow Rate {m3/s}
autosize, !- volume of the plant loop {m3}
Hot Water Loop HW Supply Inlet, !- Plant Side Inlet Node Name
Hot Water Loop HW Supply Outlet, !- Plant Side Outlet Node Name
Hot Water Loop HW Supply Side Branches, !- Plant Side Branch List Name
Hot Water Loop HW Supply Side Connectors, !- Plant Side Connector List Name
Hot Water Loop HW Demand Inlet, !- Demand Side Inlet Node Name
Hot Water Loop HW Demand Outlet, !- Demand Side Outlet Node Name
Hot Water Loop HW Demand Side Branches, !- Demand Side Branch List Name
Hot Water Loop HW Demand Side Connectors, !- Demand Side Connector List Name
SequentialLoad, !- Load Distribution Scheme
, !- AvailabilityManagerAssignmentList
SingleSetpoint; !- Plant Loop Demand Calculation Scheme
PlantEquipmentOperationSchemes,
Hot Water Loop Operation, !- Name
PlantEquipmentOperation:HeatingLoad, !- Control Scheme Object Type
Hot Water Loop Operation All Hours, !- Control Scheme Name
HVACTemplate-Always 1; !- Control Scheme Schedule Name
Hot Water Loop Operation All Hours, !- Name
0, !- Load Range Lower Limit 1 {W}
1000000000000000, !- Load Range Upper Limit 1 {W}
Hot Water Loop All Equipment; !- Priority Control 1 Equipment List Name
PlantEquipmentList,
Hot Water Loop All Equipment, !- Name
Boiler:HotWater, !- Equipment Object Type
Main Boiler; !- Equipment Name
NodeList,
Hot Water Loop HW Supply Setpoint Nodes, !- Name
Main Boiler HW Outlet, !- Node Name
Hot Water Loop HW Supply Outlet; !- Node Name
SetpointManager:OutdoorAirReset,
Hot Water Loop HW Temp Manager, !- Name
Temperature, !- Control Variable
82.2, !- Set point at outside low {C}
-6.7, !- Outside low {C}
65.6, !- Set point at outside high {C}
10, !- Outside high {C}
Hot Water Loop HW Supply Setpoint Nodes; !- Setpoint Node or NodeList Name
BranchList,
Hot Water Loop HW Supply Side Branches, !- Name
Hot Water Loop HW Supply Inlet Branch, !- Name
Main Boiler HW Branch, !- Branch Name
Hot Water Loop HW Supply Bypass Branch, !- Name
Hot Water Loop HW Supply Outlet Branch; !- Name
ConnectorList,
Hot Water Loop HW Supply Side Connectors, !- Name
Connector:Splitter, !- Connector Object Type
Hot Water Loop HW Supply Splitter, !- Connector Name
Connector:Mixer, !- Connector Object Type
Hot Water Loop HW Supply Mixer; !- Connector Name
Connector:Splitter,
Hot Water Loop HW Supply Splitter, !- Name
Hot Water Loop HW Supply Inlet Branch, !- Inlet Branch Name
Main Boiler HW Branch, !- Outlet Branch Name
Hot Water Loop HW Supply Bypass Branch; !- Outlet Branch Name
Connector:Mixer,
Hot Water Loop HW Supply Mixer, !- Name
Hot Water Loop HW Supply Outlet Branch, !- Outlet Branch Name
Hot Water Loop HW Supply Bypass Branch; !- Inlet Branch Name
Branch,
Pipe:Adiabatic, !- Component Object Type
Hot Water Loop HW Supply Side Bypass Pipe, !- Component Name
Hot Water Loop HW Supply Bypass Inlet, !- Component Inlet Node Name
Hot Water Loop HW Supply Bypass Outlet, !- Component Outlet Node Name
Bypass; !- Component Branch Control Type
Pipe:Adiabatic,
Hot Water Loop HW Supply Side Bypass Pipe,!- Name
Hot Water Loop HW Supply Bypass Inlet, !- Inlet Node Name
Hot Water Loop HW Supply Bypass Outlet; !- Outlet Node Name
Pump:ConstantSpeed,
Hot Water Loop HW Supply Pump, !- Name
Hot Water Loop HW Supply Inlet, !- Inlet Node Name
Hot Water Loop HW Pump Outlet, !- Outlet Node Name
autosize, !- Rated Volumetric Flow Rate {m3/s}
179352, !- Rated Pump Head {Pa}
autosize, !- Rated Power Consumption {W}
0.9, !- Motor Efficiency
0, !- Fraction of Motor Inefficiencies to Fluid Stream
; !- Pump Flow Rate Schedule Name
Branch,
Pump:ConstantSpeed, !- Component Object Type
Hot Water Loop HW Supply Pump, !- Component Name
Hot Water Loop HW Supply Inlet, !- Component Inlet Node Name
Hot Water Loop HW Pump Outlet, !- Component Outlet Node Name
Branch,
Hot Water Loop HW Supply Outlet Branch, !- Name
Hot Water Loop HW Supply Outlet Pipe, !- Component Name
Hot Water Loop HW Supply Outlet Pipe Inlet, !- Component Inlet Node Name
Hot Water Loop HW Supply Outlet, !- Component Outlet Node Name
Passive; !- Component Branch Control Type
Pipe:Adiabatic,
Hot Water Loop HW Supply Outlet Pipe, !- Name
Hot Water Loop HW Supply Outlet Pipe Inlet, !- Inlet Node Name
Hot Water Loop HW Supply Outlet; !- Outlet Node Name
BranchList,
Hot Water Loop HW Demand Side Branches, !- Name
Hot Water Loop HW Demand Inlet Branch, !- Name
Hot Water Loop HW Demand Bypass Branch, !- Name
Hot Water Loop HW Demand Outlet Branch; !- Name
ConnectorList,
Hot Water Loop HW Demand Side Connectors, !- Name
Hot Water Loop HW Demand Splitter, !- Connector Name
Hot Water Loop HW Demand Mixer; !- Connector Name
Connector:Splitter,
Hot Water Loop HW Demand Splitter, !- Name
Hot Water Loop HW Demand Inlet Branch, !- Inlet Branch Name
Hot Water Loop HW Demand Bypass Branch, !- Outlet Branch Name
SPACE1-1 Baseboard Heat HW Branch; !- Name
Connector:Mixer,
Hot Water Loop HW Demand Mixer, !- Name
Hot Water Loop HW Demand Outlet Branch, !- Outlet Branch Name
Hot Water Loop HW Demand Bypass Branch, !- Inlet Branch Name
Branch,
Hot Water Loop HW Demand Inlet Pipe, !- Component Name
Hot Water Loop HW Demand Inlet, !- Component Inlet Node Name
Hot Water Loop HW Demand Inlet Pipe Outlet, !- Component Outlet Node Name
Pipe:Adiabatic,
Hot Water Loop HW Demand Inlet Pipe, !- Name
Hot Water Loop HW Demand Inlet, !- Inlet Node Name
Hot Water Loop HW Demand Inlet Pipe Outlet; !- Outlet Node Name
Branch,
Hot Water Loop HW Demand Side Bypass Pipe, !- Component Name
Hot Water Loop HW Demand Bypass Inlet, !- Component Inlet Node Name
Hot Water Loop HW Demand Bypass Outlet, !- Component Outlet Node Name
Pipe:Adiabatic,
Hot Water Loop HW Demand Side Bypass Pipe, !- Name
Hot Water Loop HW Demand Bypass Inlet, !- Inlet Node Name
Hot Water Loop HW Demand Bypass Outlet; !- Outlet Node Name
Branch,
Hot Water Loop HW Demand Outlet Branch, !- Name
Hot Water Loop HW Demand Outlet Pipe, !- Component Name
Hot Water Loop HW Demand Outlet Pipe Inlet, !- Component Inlet Node Name
Hot Water Loop HW Demand Outlet, !- Component Outlet Node Name
Pipe:Adiabatic,
Hot Water Loop HW Demand Outlet Pipe, !- Name
Hot Water Loop HW Demand Outlet Pipe Inlet, !- Inlet Node Name
Hot Water Loop HW Demand Outlet; !- Outlet Node Name
Site:GroundTemperature:BuildingSurface,
21.5, !- January Ground Temperature
21.4, !- February Ground Temperature
21.5, !- March Ground Temperature
21.5, !- April Ground Temperature
22.0, !- May Ground Temperature
22.9, !- June Ground Temperature
23.0, !- July Ground Temperature
23.1, !- August Ground Temperature
23.1, !- September Ground Temperature
22.2, !- October Ground Temperature
21.7, !- November Ground Temperature
21.6; !- December Ground Temperature
! 1, !- Priority
ScheduleTypeLimits,
Schedule:Compact,
1; !- Field 4
Schedule:Compact,
4; !- Field 4
Sizing:Zone,
Branch,
Boiler:HotWater,
Curve:Quadratic,
Branch,
Sizing:Plant,
PlantLoop,
PlantEquipmentList,
NodeList,
BranchList,
ConnectorList,
Connector:Splitter,
Connector:Mixer,
Branch,
Pipe:Adiabatic,
Pump:ConstantSpeed,
Branch,
Branch,
Pipe:Adiabatic,
BranchList,
ConnectorList,
Connector:Splitter,
Connector:Mixer,
Branch,
Pipe:Adiabatic,
Branch,
Pipe:Adiabatic,
Branch,
Pipe:Adiabatic,
! 1, !- Priority
ScheduleTypeLimits,
Schedule:Compact,
1; !- Field 4
Schedule:Compact,
4; !- Field 4
Sizing:Zone,
Branch,
Boiler:HotWater,
Curve:Quadratic,
Branch,
Sizing:Plant,
PlantLoop,
PlantEquipmentList,
NodeList,
BranchList,
ConnectorList,
Connector:Splitter,
Connector:Mixer,
Branch,
Pipe:Adiabatic,
Pump:ConstantSpeed,
Branch,
Branch,
Pipe:Adiabatic,
BranchList,
ConnectorList,
Connector:Splitter,
Connector:Mixer,
Branch,
Pipe:Adiabatic,
Branch,
Pipe:Adiabatic,
Branch,
Pipe:Adiabatic,
| 4 | No.4 Revision |
The current template expansion program supports the following objects. These are the plant, system, thermostat, and zone templates. Typically, one of each of these is required. The plant type is used when chilled or hot water loops are needed. If there are no plant loops, this template is not used. The system type is used for each HVAC system. system configured as air loop equipment. The thermostat type is used to populate the zones with a thermostat. And finally, the zone type is used for zone equipment in each zone.
! 1, !- Priority
ScheduleTypeLimits,
Schedule:Compact,
1; !- Field 4
Schedule:Compact,
4; !- Field 4
Sizing:Zone,
Branch,
Boiler:HotWater,
Curve:Quadratic,
Branch,
Sizing:Plant,
PlantLoop,
PlantEquipmentList,
NodeList,
BranchList,
ConnectorList,
Connector:Splitter,
Connector:Mixer,
Branch,
Pipe:Adiabatic,
Pump:ConstantSpeed,
Branch,
Branch,
Pipe:Adiabatic,
BranchList,
ConnectorList,
Connector:Splitter,
Connector:Mixer,
Branch,
Pipe:Adiabatic,
Branch,
Pipe:Adiabatic,
Branch,
Pipe:Adiabatic,