From the figure, it appears to show a split-system configured in an air loop, and a fan coil used as zone equipment. In EnergyPlus, air loop equipment are always simulated first. Zone equipment is simulated next and picks up (or adds to) the remaining zone load, if any.
Regarding the operation of each of these equipment, the availability schedule can be used to turn the systems on and off using a schedule. For air loop equipment, availability schedules can be applied at the air loop, system, coil, or fan level.
AirLoopHVAC,
Typical Furnace 1, !- Name
, !- Controller List Name
Furnace 1 Avail List, !- Availability Manager List Name
AirLoopHVAC:Unitary:Furnace:HeatCool,
GasHeat DXAC Furnace 1, !- Name
FanAndCoilAvailSched, !- Availability Schedule Name
Coil:Cooling:DX:SingleSpeed,
Furnace ACDXCoil 1, !- Name
Fan:OnOff,
Supply Fan 1, !- Name
Similar for zone equipment, a system, coil, or fan level availability schedule may be used.
ZoneHVAC:FourPipeFanCoil,
Zone1FanCoil, !- Name
Coil:Cooling:Water,
Zone1FanCoilCoolingCoil, !- Name
Fan:ConstantVolume,
Zone1FanCoilFan, !- Name
Typically, systems and coils are scheduled on all the time and the fans are scheduled to be available as needed. This way, the night cycle availability managers can override the fan schedules and turn on system to condition the building at night as needed.
Noting the outdoor air in the figure, the fan can either be available all the time, or can be scheduled off at night and enabled (overridden) using the night cycle air loop availability manager (AvailabilityManager:NightCycle).
AirLoopHVAC,
VAV Sys 1, !- Name
VAV Sys 1 Controllers, !- Controller List Name
VAV Sys 1 Avail List, !- Availability Manager List Name
AvailabilityManagerAssignmentList,
VAV Sys 1 Avail List, !- Name
AvailabilityManager:NightCycle, !- Availability Manager 1 Object Type
VAV Sys 1 Avail; !- Availability Manager 1 Name
VAV Sys 1 Avail, !- Name
SysAvailApplicSch, !- Applicability Schedule Name
FanAvailSched, !- Fan Schedule Name
CycleOnAny, !- Control Type
1, !- Thermostat Tolerance {deltaC}
7200.; !- Cycling Run Time {s}
The schedules for the air loop and fan coil should use opposing values where a 1 (on) is used in one case, and a 0 (off) in the other case.
From the figure, it appears to show a split-system configured in an air loop, and a fan coil used as zone equipment. In For those interested in the equipment simulation order, in EnergyPlus, air loop equipment are always simulated first. Zone equipment is are simulated next and picks up (or adds to) the remaining zone load, if any. The zone equipment also has a priority based on the entry in the ZoneHVAC:EquipmentList object. Only a single zone equipment is listed in this example, however, multiple zone equipment objects can be listed and given operational priority as needed.
ZoneHVAC:EquipmentConnections,
EAST ZONE, !- Zone Name
Zone2Equipment, !- Zone Conditioning Equipment List Name
Zone2Inlets, !- Zone Air Inlet Node or NodeList Name
Zone2Exhausts, !- Zone Air Exhaust Node or NodeList Name
Zone 2 Node, !- Zone Air Node Name
Zone 2 Outlet Node; !- Zone Return Air Node Name
ZoneHVAC:EquipmentList,
Zone2Equipment, !- Name
ZoneHVAC:FourPipeFanCoil,!- Zone Equipment 1 Object Type
Zone2FanCoil, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Sequence
1; !- Zone Equipment 1 Heating or No-Load Sequence
AirLoopHVAC,
Fan:OnOff,
Coil:Cooling:Water,
Fan:ConstantVolume,
AirLoopHVAC,
VAV Sys 1, !- Name
From the figure, it appears to show a split-system configured in an air loop, and a fan coil used as zone equipment. For those interested in the equipment simulation order, in EnergyPlus, air loop equipment are always simulated first. Zone equipment are simulated next and picks up (or adds to) the remaining zone load, if any. The zone equipment also has a priority based on the entry in the ZoneHVAC:EquipmentList object. Only a single zone equipment is listed in this example, however, multiple zone equipment objects can be listed and given operational priority as needed.
AirLoopHVAC,
Fan:OnOff,
Coil:Cooling:Water,
Fan:ConstantVolume,
AirLoopHVAC,
VAV Sys 1, !- Name
The To operate one equipment (e.g., air loop) at different times than another (e.g., zone equipment), the schedules for the air loop and fan coil should use opposing values where a 1 (on) is used in one case, and a 0 (off) in the other case.
| 4 | No.4 Revision |
AirLoopHVAC,
Fan:OnOff,
Fan Coil Availability Manager; !- Availability Manager List Name
Coil:Cooling:Water,
Fan:ConstantVolume,
AirLoopHVAC,
VAV Sys 1, !- Name
| 5 | No.5 Revision |
AirLoopHVAC,
Fan:OnOff,
Coil:Cooling:Water,
Fan:ConstantVolume,
AirLoopHVAC,
VAV Sys 1, !- Name