I suggest you review the VRF performance curve(s) for EIR. You might input a 3.5 COP, however, as outdoor temperatures fall, the EIR also falls due to the cold weather.
Plot the curve results versus outdoor wet-bulb temperature (or dry-bulb depending on the input field Heating Performance Curve Outdoor Temperature Type). Also include a range of indoor dry-bulb temperatures to see the impact of all possible operation conditions within your simulation/geography. See Figure 7 in http://www.fsec.ucf.edu/en/publications/pdf/FSEC-CR-1910-12.pdf
AirConditioner:VariableRefrigerantFlow,
  VRFHeatEIRFT,    !- Heating Energy Input Ratio Modifier Function of Low Temperature Curve Name
  VRFHeatEIRFTBoundary,    !- Heating Energy Input Ratio Boundary Curve Name
  VRFHeatEIRFTHi,  !- Heating Energy Input Ratio Modifier Function of High Temperature Curve Name
  WetBulbTemperature,      !- Heating Performance Curve Outdoor Temperature Type
Curve:Biquadratic,
  VRFHeatEIRFT,            !- Name
  0.87465501,              !- Coefficient1 Constant
  -0.01319754,             !- Coefficient2 x
  0.00110307,              !- Coefficient3 x**2
  -0.0133118,              !- Coefficient4 y
  0.00089017,              !- Coefficient5 y**2
  -0.00012766,             !- Coefficient6 x*y
  15,                      !- Minimum Value of x
  27,                      !- Maximum Value of x
  -20,                     !- Minimum Value of y
  12,                      !- Maximum Value of y
click to hide/show revision 2
No.2 Revision
I suggest you review the VRF performance curve(s) for EIR. You might input a 3.5 COP, however, as outdoor temperatures fall, the EIR also falls due to the cold weather. It is not uncommon for heat pumps to perform poorly with low COPs in cold weather.
Curve:Biquadratic,
click to hide/show revision 3
No.3 Revision
Curve:Biquadratic,