In fact, there is a way around this bug to some extent, but not completely.
Multiple PlantEquipmentList objects can be modelled as follows to allow operation of only one chiller, two chillers, three chillers , and all chillers. The load upper limit for each PlantEquipmentList object is specified in PlantEquipmentOperation:CoolingLoad.
PlantEquipmentList,
Chilled Water Loop 1 Chiller, !- Name
Chiller:Electric:EIR, !- Equipment 1 Object Type
Chiller1; !- Equipment 1 Name
PlantEquipmentList,
Chilled Water Loop 2 Chillers, !- Name
Chiller1, !- Equipment 1 Name
Chiller:Electric:EIR, !- Equipment 2 Object Type
Chiller2; !- Equipment 2 Name
PlantEquipmentList,
Chilled Water Loop 3 Chillers, !- Name
Chiller2, !- Equipment 2 Name
Chiller:Electric:EIR, !- Equipment 3 Object Type
Chiller3; !- Equipment 3 Name
PlantEquipmentList,
Chilled Water Loop All Chillers, !- Name
Chiller3, !- Equipment 3 Name
Chiller:Electric:EIR, !- Equipment 4 Object Type
Chiller4; !- Equipment 4 Name
PlantEquipmentOperation:CoolingLoad,
Chilled Water Loop Chiller Operation All Hours, !- Name
0, !- Load Range 1 Lower Limit {W}
8866.94, !- Load Range 1 Upper Limit {W}
Chilled Water Loop 1 Chiller, !- Range 1 Equipment List Name
8866.94, !- Load Range 2 Lower Limit {W}
17733.88, !- Load Range 2 Upper Limit {W}
Chilled Water Loop 2 Chillers, !- Range 2 Equipment List Name
17733.88, !- Load Range 3 Lower Limit {W}
26600.82, !- Load Range 3 Upper Limit {W}
Chilled Water Loop 3 Chillers, !- Range 3 Equipment List Name
26600.82, !- Load Range 4 Lower Limit {W}
1E+15, !- Load Range 4 Upper Limit {W}
Chilled Water Loop All Chillers; !- Range 4 Equipment List Name
However, when a large negative value is detected in the output variable Plant Supply Side Unmet Demand Rate, Plant Supply Side Cooling Demand Rate gets bigger than it needs to be, and this workaround does not work well.