|  1 |    initial version    |
The plant water temperature is not hot enough to heat the air passing through this coil up to Controller temperature setpoint = 11.95 [C] when the HW coil entering water temperature is Controller actuator temperature = -8.06 [C]. Here the HW coil entering air temperature is Controller sensed temperature = -2.53 [C]. So this issue is with the plant equipment not controlling the plant water temperature properly. i.e., the problem is not with the HW coil controller.
    |  2 |    No.2 Revision    |
The plant water temperature is not hot enough to heat the air passing through this coil up to Controller temperature setpoint = 11.95 [C] when the HW coil entering water temperature is Controller actuator temperature = -8.06 [C]. Here the HW coil entering air temperature is Controller sensed temperature = -2.53 [C]. So this issue is with the plant equipment not controlling the plant water temperature properly. i.e., the problem is not with the HW coil controller.controller. Look into why the plant CentralHeatPumpSystem is not working properly.