Question-and-Answer Resource for the Building Energy Modeling Community
Get started with the Help page
Ask Your Question
1

What depth does the Site:GroundTemperature:Undisturbed:KusudaAchenbach object assume is being considered?

asked 2020-02-21 11:01:09 -0500

updated 2020-02-21 11:36:52 -0500

I am using this object to model ground temperature for a vertical borefield ground heat exchanger as part of a GSHP plant. I am curious to know if this calculation model makes a built-in assumption about the depth at which heat transfer is being calculated, as it is does not appear to be a property that I can specify within the object parameters.

The only place in the model that this object is referenced is in the Undisturbed Ground Temperature Model Type property within the GroundHeatExchanger:System object. The only other alternative to a built-in depth assumption that I can imagine is that the model somehow uses the heat exchanger depth (either average depth or continuously over it's length), in the GroundHeatExchanger:Vertical:Properties object, as the depth at which ground temperature is calculated.

Thanks!

image description

edit retag flag offensive close merge delete

Comments

I think Kusuda-Achenbach is just a model of temperature in the ground and doesn't have a specific depth or temperature. It is the ground heat exchanger that would be requesting temperatures at various depths. I would suggest you read the documentation on the components you are using in the Engineering Reference to get a better understanding.

JasonGlazer's avatar JasonGlazer  ( 2020-02-26 08:56:43 -0500 )edit

1 Answer

Sort by ยป oldest newest most voted
1

answered 2026-04-06 22:58:10 -0500

"The correlation uses three parameters for ground temperature at the surface to define a correlation for undisturbed ground temperatures as a function of depth and time. If one thinks of the ground temperature for a given depth as a sinusoid, the average ground temperature, amplitude (average difference between maximum ground temperature and minimum ground temperature), and the phase shift (day of minimum surface temperature) are all required to define the correlation.

If the parameters are left blank they can be autocalculated by including soil surface temperatures in the input using the Site:GroundTemperature:Shallow object. They can also be calculated by using the CalcSoilSurfTemp preprocessor."

https://bigladdersoftware.com/epx/doc...

edit flag offensive delete link more