asked 2018-01-05 15:33:11 -0600
updated 2018-01-07 08:54:16 -0600
We are modelling buildings with high people density where latent heat gain cannot be ignored. Any idea how to implement latent heat gain with TRNSYS Type 56?
As far as i remember there is an option in the gains menu where you can specify the latent fraction.
answered 2018-01-11 09:29:02 -0600
Latent gains are added in Type56 as a humidity gain in kg/h. The input is on the gain definition window in TRNBuild.
Please start posting anonymously - your entry will be published after you log in or create a new account.
Add Answer
subscribe to rss feed