How humidity is controled in HVACTemplate:System:VAV
I modeled VAV for air side with water cooled chiller for water side using HVACTemplate.
In HVACTemplate:System:VAV, I set Dehumidification Control type:CoolReheat,Dehumidification Setpoint:50%.
However, when I look at result, humidity seems strangely low (sometimes it reaches to 20%) in summer compared to the climate data.
(below image shows annual humidity data left:Outdoor, right:conditioned area)
Can anyone tell me what is causing such a low humidity control?


If point 1 is further right and point 3 is further left, RH could be same or higher as a result of cooling and dehumidification. Plotting temperature and humidity ratio instead of RH at various air loop nodes from expidf file will show why zone is not maintaining RH setpoint. It could be that even if the outside RH is high, the outside humidity ratio is low during winter and zone moisture load is not enough to hit the RH setpoint. If this is the case, then adding humidifier may help improve the results. Once the air gets saturated though, RH setpoint would still not be met during winter. Running model at different weather locations would also help understand the results.

