In ENrgyPlus, Is there a way to create EnergyManagementSystem:Actuator with Actuated component type Coil:Heating:Electric and control type as Nominal capacity?

asked 2025-08-07 05:53:58 -0500

Venu's avatar

updated 2025-08-07 11:09:30 -0500

In ENrgyPlus, Is there a way to create EnergyManagementSystem:Actuator with Actuated component type Coil:Heating:Electric and control type as Nominal capacity?

edit retag flag offensive close merge delete

1 Answer

Sort by ยป oldest newest most voted
0

answered 2025-08-07 20:17:53 -0500

Greg Estep's avatar

I don't think so. Coil:Heating:Electric says If used in the air loop simulation it will be controlled to a specified temperature scheduled from the SetPoint Manager. If it is used in zone equipment, it will be controlled from the zone thermostat by meeting the zone demand.

Per the EnergyManagementSystem:Actuator, The control types available are listed in the EDD output.

edit flag offensive delete link more

Comments

Thanks Greg Estep, for taking time on this post and answering it.

Venu's avatar Venu  ( 2025-08-07 23:19:43 -0500 )edit