Clarification on Modeling Solar Hot Water Systems in ASHRAE 90.1-2010 Baseline

asked 2025-07-08 05:13:59 -0500

Anurag_G's avatar

For a LEED energy model following ASHRAE 90.1-2010 Appendix G, we're modeling a domestic solar hot water system with:

3 flat plate collectors Solar storage tank Showers as primary end-use

Proposed Case: Modelled the actual solar thermal system

Baseline Case:

Does ASHRAE 90.1-2010 require the baseline to: a) Include an identical solar thermal system? b) Use a conventional system (electric/gas water heater) instead? c) Follow some prescriptive solar requirements?​

Reference to specific sections in ASHRAE 90.1-2010 would be greatly appreciated.

edit retag flag offensive close merge delete

2 Answers

Sort by » oldest newest most voted
0

answered 2025-07-10 13:20:39 -0500

Greg Estep's avatar

updated 2025-07-10 13:21:15 -0500

Hi Anurag, I'm finding ChatGPT to be excellent at answering 90.1 questions. https://chatgpt.com/share/e/6870044e-...

edit flag offensive delete link more
0

answered 2025-07-10 22:22:18 -0500

Anurag_G's avatar

Hi Greg, I found the below comment on chatgpt. My point is we have a 100% solar hot water system without any backup systems like electric water heaters. Do we only realize the complete savings by modelling the solar hot water system on proposed model and not modelling anything on baseline model? Appreciate your response!!

*"The baseline building shall use the same service water heating system type (e.g., electric resistance, gas-fired storage, etc.) as the proposed design, except that renewable energy systems (e.g., solar thermal) shall not be included in the baseline building design. *Interpretation for Your Case Proposed Case: You correctly modeled the actual solar thermal system. Baseline Case: You should not include the solar thermal system. Instead, model a conventional system (e.g., electric or gas water heater) that meets the minimum efficiency requirements specified."**

edit flag offensive delete link more

Comments

1

Ah, interesting. I think you should take the largest credit you can. For LEED, points are based on energy cost. Thus, I would set the baseline service water heating system as electric resistance and meet the minimum efficiency requirements. This is because electricity is so much more expensive than fossil fuels (at least in the Northeast of USA). This way, you will maximize points. Does your model show that the solar hot water systems always meets the demand?

Greg Estep's avatar Greg Estep  ( 2025-07-11 15:40:51 -0500 )edit

Hi Greg, thanks for your response. The domestic hot water are serving mostly the showers and some kitchens. In India, hot water requirement is quite less, mostly during the winters. So, demands are quite meeting. What I had approached was considering the solar hot water system in proposed case while not considering any service hot water system in baseline since this case is not well defined in LEED. Though the savings wouldn't be maximized as you said, but I would atleast not be missing on the solar hot water savings.

Anurag_G's avatar Anurag_G  ( 2025-07-12 08:29:08 -0500 )edit