AddWindAndStackOpenArea

asked 2022-02-12 23:58:49 -0500

Bill's avatar

I have recently updated from OpenStudio 3.2.1 to 3.3.0 and models that ran okay previously now fail and give the following message when using this EnergyPlus measure. They run properly without the measure.

"No windows found in selection matching given construction. This means your model lacks windows or lacks windows with the specified construction."

Has anyone else run into the problem and what is the likely cause?

edit retag flag offensive close merge delete

Comments

Have you confirmed that the user argument value for construction has not changed? What is that value? Specifically is it blank which would apply to all operable windows instead of just operable windows of a specific construction. Also is surface type still set to operable window instead of fixed window?

David Goldwasser's avatar David Goldwasser  ( 2022-02-14 01:02:02 -0500 )edit

Thanks for response. I confirm that the only change made is to add the measure. Subsurface type remains set to operable window but I am not sure how to check "user argument value for construction". I am using the OpenStudio application.

Bill's avatar Bill  ( 2022-02-19 21:51:01 -0500 )edit